What is the By-pass factor for cooling coil, if td$_{1}$ = 49°C, td$_{2}$ = 36°C and td$_{3}$ = 30°C?

Minh Phượng

New member
What is the By-pass factor for cooling coil, if td$_{1}$ = 49°C, td$_{2}$ = 36°C and td$_{3}$ = 30°C?
A. 0.315
B. 0.31
C. 0.320
D. 0.3
 
Answer: a
Explanation: By-pass factor is the amount of air by-passed in the process. So, for the cooling coil,
BPF = Temperature difference between exit and coil / Temperature difference between entry and coil
= td$_{2}$ – td$_{3}$ / td$_{1}$ – td$_{3}$
= 36 – 30 / 49 – 30
= 0.315.
 